I have a CMT2078x panel application and a Schneider Modicon 241 PLC; the two devices communicate using the Schneider SoMachine M Series (Ethernet) protocol.
Often, when the machine is turned on, the buttons associated with the PLC variables are not displayed, and the operator has to cut the power and turn it back on (sometimes several times). Once communication is established, there are no more problems.
The system parameters are: port 1740, protocol Node name UDP (fast ethernet does’nt work), source port 1742, timeout 1.0, delay 300ms, resend 3 times; uses flagged UDP.
Good morning! Thank you for your question. When the issue occurs, are there any other objects in the project that are tied to the PLC and still displayed correctly, aside from the buttons?
If possible, please provide screenshots of the HMI when the issue occurs, as well as any communication/error messages.
Additionally, we typically recommend leaving the turn-around delay at its default setting of 0 ms and the timeout at 5.0 seconds, as changing these settings can sometimes affect communication efficiency. As a troubleshooting step, please try the default settings to see if the issue persists.
Hi, the machinery is far away, I’ll try next week to make these changes. It’s just the variables that aren’t made available, and sometimes the communication failure popup appears.
When you are able to access the machine, we also recommend following the steps in the PLC Connection Guide for the Schneider SoMachine M Series (Ethernet) protocol, as well as re-importing the PLC tags to ensure the latest tag configuration is being used.
Here is the PLC Connection Guide for your reference: link.
Please let us know what you find, and we’ll be happy to assist further.