Can you delay event monitoring past 120 seconds?

Can you delay event monitoring past 120 seconds?
none 0.0 0

Hi,

In the event alarm log we can delay the event monitoring but it goes up to 120 seconds only, is there a way to make it delay 10 minutes?

On the system I am using It usually takes around 5-6 minutes for our system to prime and stabilize after that we can start monitoring for alarms, otherwise I get false alarms at the start of the system.

Thanks

Hi @gary14,

I would suggest that you configure an “Enable/Disable” bit within each alarm that you would like to delay:
image

Then, you can use a Macro similar to the one defined below to delay the time of event monitoring well past 120 seconds:
Note: “Execute one time when HMI starts” is enabled.

1 Like

That did it ! Thank you !