Click PLC Connectivity Issues

Click PLC Connectivity Issues
none 0.0 0

I recommend you give this a try.

IP addresses as follows:
ClickPLC: 192.168.254.192 (Subnet mask 255.255.255.0)
Development Computer: 192.168.254.11 (Subnet mask 255.255.255.0)
SVR-100 Port 1: 192.168.254.175 (Static) (Subnet mask 255.255.255.0)
SVR-100 Port 2: Not used. The IP address must be a different subnet such as 192.168.100.1

Wiring is as follows:
SVR-100: direct connection to switch (Please connect CMT-SVR port 1 to the switch)
ClickPLC: direct connection to switch
Development Computer: direct connection to switch