- HMI Model: cMT2078
- EasyBuilder Pro Version: 6.10.02
Does anyone have experience with setting up the communications between the cMT2078 and Yaskawa’s new iCube controller (iC9226M-EC)? The iCube controller supports Ethernet/IP, ModbusTCP, and OPC UA. They push using OPC UA, but I don’t see that a connection can be made in EasyBuilder Pro to a OPC UA server.
Thank you.
Hi @patrick ,
Thank you for your question. To better understand your setup, could you clarify whether the PLC is acting as the server or the client?
It is acting as the server.
Hi @patrick ,
Thank you for the additional information!
In that case, you can use the OPC UA Client driver to connect to the controller. The following video provides a step-by-step walkthrough of the setup process:
How to Connect to OPC UA Server
Thank you, Arden. I will review the video and the server’s documentation to set it up.
Hello, l have been able to establish connection between the cMT2078V2 and the Yaskawa iCube Controller, but when I connect to select the tags EasyBuilder Pro 6.10 only sees those tags that are considered global. I have several local tags within separate POUs that it does not see even when I select in the Yaskawa development software to have it included in the OPC UA “table.” Thoughts?
Hi @patrick ,
Thank you for your follow-up question! Are you able to download a third-party OPC UA client, such as UaExpert, and connect directly to the PLC’s OPC UA server to see whether the local POU tags are visible there?
I have downloaded UaExpert and am going through setting it up to test. I will contact you back next week.