How to connect MT8072iP to a SLC 5/04

How to connect MT8072iP to a SLC 5/04
none 0.0 0

Is there a way to get help with troubleshooting communications between a mt8072iP and slc504, or am I confined to a sea of unrelated topics in the forum?

Hi @clangkamp ,

Thank you for you question.

I will link documentation below to 3 drivers that support the SLC 5/04 below. Please check these instructions.

If you are still having issue could you describe what the problem is and upload screen shots of any error codes that come up as well as you setup.

Thank you!

Rockwell Ethernet IP Setup

Rockwell DH485 Setup

Rockwell DF1 Setup

the 5/04 doesn’t support Ethernet.. that would need to be a 5/05… so you are probably using the serial port on the 5/04… or you could be using a very old KF unit which goes from serial to DH+. If you are using the serial port you need to see how its setup.. could be DF1 or DH485.. if only the Weintek is connected to the port, you should use DF1… and you should post the port setup so others can determine how the Weintek needs to be configured and the cabling required. Bob

1 Like