  • How do I create a running elapsed time timer using a macro? Or is there a better way of displaying elapsed time?

Hi @leadfoote ,

One way to display elapsed time is by using the timer object, which can be found under the Object tab. If you want the timer to work across all windows, select the global version; if you only need it on one page, choose the per-page timer.

For the Mode of the timer, I recommend selecting either On delay or Accumulated On delay. Both will start the timer when the input bit is turned ON. The key difference is that Accumulated On delay retains the elapsed time when the input bit is turned off before ET reaches the PT. When On delay is used and the input bit is turned off before ET reaches the PT, the ET will reset to 0.

Additionally, enable the Elapsed time memory register to view the elapsed time, and assign it to a free memory register. You will also need to set a Preset time, which determines the maximum value your timer will count to. The maximum value for the preset timer is 86400 seconds. This can be a constant value or linked to a memory register for dynamic control.

Please let me know if this solution meets your project goals. If not, could you please describe how you are want to record the elapsed time? That way, we can recommend the best approach for your needs.

Thanks for getting back to me!
I need to show elapsed time for much longer than 24 hours possibly weeks. I was thinking I may have to use the timer combined with a counter? Maybe I need to use a macro? Thanks

Hi @leadfoote ,

Yes, if you wanted to hold weeks, it would be a combination of the timer object and macros. I was curious about how precise you needed the count to be. Are you only displaying the weeks and days, or something finer like hours, minutes, and seconds for your elapsed time?

Thank you!

I need to display days, hours, minutes and seconds.

Hi @leadfoote,

Yes, you were correct , using macros was the best solution, as we can utilize the HMI’s system time to calculate the elapsed time. The system time can be accessed through LW-9030, which is a system address tag.

Below is the macro we used. It sets up variables for the start time (at the beginning of execution) and the current time. By subtracting these values, we get the elapsed time. Dividing the result by 10 modifies the value into seconds as the periodical execution is set to 10x100ms . We then display the hours, minutes, and seconds using division and modulus operations.

Additionally, a toggle switch is set at LB-0 to reset the values and start the timer when needed. To achieve this, we store the start value in LW-8999.

Here is also the project if needed: Project

macro_command main()

	// Variable Set up
	unsigned int start = 0, now = 0, result = 0 
	bool trigger
	short total_seconds, hours, minutes, seconds
	
	// Grab the trigger and start values from HMI memory address
	GetData(trigger, "Local HMI", LB, 0,1)
	GetData(start, "Local HMI", LW, 8999, 1) 
	
	
	// Trigger is LB 0 to start the timer
	if trigger then
	
	// check if start is 0, if it is grab the time for current and place it within a HMI memory address. 
	if start == 0 then
	GetData(start, "Local HMI", LW, 9030, 1) 	
	SetData(start, "Local HMI", LW, 8999, 1)
	end if 
	
	
	// grab the current value. 
	GetData(now, "Local HMI", LW, 9030, 1) 
	result =now - start
	
	
	
	// calc hour, minute, second based on result / 10
	// ADD more calucations here for days, weeks and years if needed. 
	
	
	// set the seconds
	total_seconds = result/10
	seconds = total_seconds %60
	SetData(seconds, "Local HMI", LW, 0, 1)
	
	// set the mins
	minutes = (total_seconds % 3600)/60
	SetData(minutes,"Local HMI",LW,1,1)
	
	// set the hours
	hours = total_seconds /3600
	SetData(hours,"Local HMI",LW,2,1)
	
	
	
	else // if trigger is off, then reset all values back to default values
	start =0
	SetData(start, "Local HMI", LW, 8999, 1)
	
	end if
	
	
	
end macro_command

AaronS

Thank you for your help! I spent three days working on this and couldn’t figure it out, you guys are miracle workers!

1 Like

Hi @leadfoote ,

We are glad this solution worked for your project! Please don’t hesitate to reach out if any other questions come up!

All the best!

Aaron,

I actually have one more question. How do I combine the hour, minute and seconds and display them on one line? Displayed like 12:34:56 HR:MIN:SEC

Hi @leadfoote

To combine the hours, minutes, and seconds within one line or memory space, we need to convert the integer values of each variable to strings. We can then take these strings and concatenate them into the correct format. Within our macro function, we have the DEC2ASCII function, which will convert integers to ASCII values for us. Then we can use the StringCat function to format all the strings in the desired order.

Please note that within the code below, I placed the final version of the string within the char array named answer. Then I used the StringSet function to place the correctly formatted string within the LW-20 memory address. This is tied to an ASCII object.

ADDED CODE

// make the correct string //
	
	// place holders for the string versions of hour,min, and seconds. 
	char hour_char[10]
	char minutes_char[10]
	char seconds_char[10]
	
	
	
	// place int to ascii values within the char arrays
	// The DEC2ASCII function will turn the int values into strings for us to use later. 
	DEC2ASCII(hours, hour_char[0], 2)
	DEC2ASCII(minutes, minutes_char[0], 2)
	DEC2ASCII(seconds, seconds_char[0], 2)
	
	// make the correct string place in ascii object
	
	char answer[100] // final string that will hold the string to set to LW 20
	char colon[2] = ":" // colon to add to string 
	
	// get the correct string -> 00:00:00
	StringCat(hour_char[0], answer[0]) // placing hour in string
	StringCat(colon[0], answer[0]) // adding a colon
	StringCat(minutes_char[0], answer[0]) // placing minutes in the string
	StringCat(colon[0], answer[0]) // adding a colon
	StringCat(seconds_char[0], answer[0]) // placing seconds in the string
	
	
	
	// Placing string in LW 20
	StringSet(answer[0], "Local HMI", LW, 20, 14) // to add in more to the string update the size of 14 to a higher number

FULL CODE

macro_command main()

	// Variable Set up
	unsigned int start = 0, now = 0, result = 0 
	bool trigger
	short total_seconds, hours, minutes, seconds
	
	// Grab the trigger and start values from HMI memory address
	GetData(trigger, "Local HMI", LB, 0,1)
	GetData(start, "Local HMI", LW, 8999, 1) 
	
	
	// Trigger is LB 0 to start the timer
	if trigger then
	
	// check if start is 0, if it is grab the time for current and place it within a HMI memory address. 
	if start == 0 then
	GetData(start, "Local HMI", LW, 9030, 1) 	
	SetData(start, "Local HMI", LW, 8999, 1)
	end if 
	
	
	// grab the current value. 
	GetData(now, "Local HMI", LW, 9030, 1) 
	result =now - start
	
	
	
	// calc hour, minute, second based on result / 10
	// ADD more calucations here for days, weeks and years if needed. 
	
	
	// set the seconds
	total_seconds = result/10
	seconds = total_seconds %60
	SetData(seconds, "Local HMI", LW, 0, 1)
	
	// set the mins
	minutes = (total_seconds % 3600)/60
	SetData(minutes,"Local HMI",LW,1,1)
	
	// set the hours
	hours = total_seconds /3600
	SetData(hours,"Local HMI",LW,2,1)
	
	
	
	// make the correct string //
	
	// place holders for the string versions of hour,min, and seconds. 
	char hour_char[10]
	char minutes_char[10]
	char seconds_char[10]
	
	
	
	// place int to ascii values within the char arrays
	// The DEC2ASCII function will turn the int values into strings for us to use later. 
	DEC2ASCII(hours, hour_char[0], 2)
	DEC2ASCII(minutes, minutes_char[0], 2)
	DEC2ASCII(seconds, seconds_char[0], 2)
	
	// make the correct string place in ascii object
	
	char answer[100] // final string that will hold the string to set to LW 20
	char colon[2] = ":" // colon to add to string 
	
	// get the correct string -> 00:00:00
	StringCat(hour_char[0], answer[0]) // placing hour in string
	StringCat(colon[0], answer[0]) // adding a colon
	StringCat(minutes_char[0], answer[0]) // placing minutes in the string
	StringCat(colon[0], answer[0]) // adding a colon
	StringCat(seconds_char[0], answer[0]) // placing seconds in the string
	
	
	
	// Placing string in LW 20
	StringSet(answer[0], "Local HMI", LW, 20, 14) // to add in more to the string update the size of 14 to a higher number
	
	
	
	
	else // if trigger is off, then reset all values back to default values
	start =0
	SetData(start, "Local HMI", LW, 8999, 1)
	
	end if
	
	
	
end macro_command

Aaron,

When I implemented the code, it created the ASCII object like its supposed to but it only counts for one cycle and stops at 7sec and when the trigger is released and enabled again it doesn’t reset back to zero. sorry to keep bothering you with this, I’m really new to macros, I’m trying to learn.

Hi @leadfoote

No bother at all, we truly appreciate all the questions coming in!

Regarding the reset issue, please make sure to enable “Auto initialize variable” in the Macro Manager settings. This should ensure your variables reset as expected.

For your reference, here’s a link to the updated project I’m working from: Updated Project

Please let me know if you have any other questions!

Got it, that worked! Thank you!

1 Like

Aaron,

I had another scenario come up.

Is it possible to have the timer pause and hold its value when the “trigger” is off and then pickup in the same spot when the trigger is on again? And use another bit to “reset” back to zero? Like if the process needs to be paused for a moment but not have the timer reset to zero when restarted.

Hi @leadfoote

Below is a rough template that works to set the start and pause on LB-0 and reset on LB-2. Modification still may be needed.

macro_command main()

    // === Variable Setup ===
    unsigned int start = 0, now = 0, result = 0, paused_elapsed = 0
    bool trigger, was_paused, reset
    short total_seconds, hours, minutes, seconds
    bool t = true, f = false
    int hold = 0
    char colon[2] = ":"

    // === Read HMI values from memory registers ===
    GetData(trigger,       "Local HMI", LB,  0,    1)  // Pause/Run toggle
    GetData(was_paused,    "Local HMI", LB,  1,    1)  // Pause flag
    GetData(reset,         "Local HMI", LB,  2,    1)  // Reset button
    GetData(start,         "Local HMI", LW, 8999, 1)  // Stored start time
    GetData(paused_elapsed,"Local HMI", LW, 8998, 1)  // Elapsed at pause
    GetData(now,           "Local HMI", LW, 9030, 1)  // System clock (0.1s units)

    // === RESET LOGIC ===
    if reset == 1 then
        start          = 0
        paused_elapsed = 0
        result         = 0

        SetData(start,          "Local HMI", LW, 8999, 1)
        SetData(paused_elapsed, "Local HMI", LW, 8998, 1)
        SetData(f,              "Local HMI", LB,  1,    1) // clear was_paused

        // clear numeric display
        SetData(hold, "Local HMI", LW, 0, 1)
        SetData(hold, "Local HMI", LW, 1, 1)
        SetData(hold, "Local HMI", LW, 2, 1)

		char time_answer[100]
        // clear string display
        time_answer[0] = 0
        char time_char[10] = "00"
        

        StringCat(time_char[0], time_answer[0]) // placing hour in string
	    StringCat(colon[0], time_answer[0]) // adding a colon
	    StringCat(time_char[0], time_answer[0]) // placing minutes in the string
	    StringCat(colon[0],time_answer[0]) // adding a colon
	    StringCat(time_char[0], time_answer[0]) // placing seconds in the string


        StringSet(time_answer[0], "Local HMI", LW, 20, 14)


        return
    end if

    // === RUN / PAUSE LOGIC ===
    if trigger == 1 then

      
        // running
        if was_paused == 1 then
            // resume: adjust start so elapsed == paused_elapsed
            start = now - paused_elapsed
            SetData(start, "Local HMI", LW, 8999, 1)
            SetData(f,     "Local HMI", LB,  1,    1) // clear was_paused
        end if

        // initialize on first run
        if start == 0 then
            start = now
            SetData(start, "Local HMI", LW, 8999, 1)
        end if

        // update elapsed
        GetData(now, "Local HMI", LW, 9030, 1)
        result = now - start

    else  // paused
  if start <> 0 and was_paused == 0 then
    // capture elapsed
    paused_elapsed = now - start
    SetData(paused_elapsed, "Local HMI", LW, 8998, 1)
    SetData(t,           "Local HMI", LB,  1,    1)
  end if
  if start <> 0 then
    result = paused_elapsed
  end if
end if

    // === TIME CONVERSION & DISPLAY ===
    total_seconds = result / 10
    seconds       = total_seconds % 60
    minutes       = (total_seconds % 3600) / 60
    hours         = total_seconds / 3600

    SetData(seconds, "Local HMI", LW, 0, 1)
    SetData(minutes, "Local HMI", LW, 1, 1)
    SetData(hours,   "Local HMI", LW, 2, 1)

    // === TIME STRING BUILD ===
    char hour_char[10]
    char minutes_char[10]
    char seconds_char[10]
    char answer[100]
    

    DEC2ASCII(hours,   hour_char[0],    2)
    DEC2ASCII(minutes, minutes_char[0], 2)
    DEC2ASCII(seconds, seconds_char[0], 2)

    answer[0] = 0

    // get the correct string -> 00:00:00
	StringCat(hour_char[0], answer[0]) // placing hour in string
	StringCat(colon[0], answer[0]) // adding a colon
	StringCat(minutes_char[0], answer[0]) // placing minutes in the string
	StringCat(colon[0], answer[0]) // adding a colon
	StringCat(seconds_char[0], answer[0]) // placing seconds in the string
	
	
	
	// Placing string in LW 20
	StringSet(answer[0], "Local HMI", LW, 20, 14) // to add in more to the string update the size of 14 to a higher number

end macro_command

Aaron,

I appreciate your help so much! With some minor modifications I was able to get this to work for me. Thanks again!