I cannot seem to find any setting to activate the Analog output error detection (open or short circuit detection). It appears this use to be in previous versions, however not anymore? I have the error mode working correctly upon loss of comms with Modbus master. I am concerned about not having any detection of loss of signal to my valve. Does this feature exist?
iR-AM06-VI, Where is analog output detection setting?
none
0.0
0
Hi @EWALDTW ,
Thank you for your question. The iR-AM06-VI will not support this feature if the AF code on its product label is anything other than 0A. This feature was discontinued in 2022.
Thank you for the information. That is a shame. Having the ability to know if an AO is shorted or broken wire is important to me.