MODBUS RTU Device Presence Detection

MODBUS RTU Device Presence Detection
none 0.0 0

Device: cMT2108X2
Version: 6.10.01.259

I’m working on an application with several field devices off the RS485 bus using MODBUS RTU, and have been trying to identify when a device is lost on the network. I’ve been looking at using the LB-9500-LB9755 registers to monitor these, is that the intent of these registers? Is there a recommended way to monitor these using EasyBuilder?

Thanks in advance

Hi @dimmed1102,

To test or check communication, please first confirm the device no. of your device within the system parameters. Here is an example:

Note: The device no. here is ‘1’.

Knowing this will help us determine what system bits to monitor. By pressing [ctrl] + [h] while EB pro is open we can open the address library and search for “device 1”:

Note: Ensure that “System tag” is selected.

Then, expand “Communication Status and Control with Device (COM)” to view applicable addresses:

The ‘SN’ abbreviation stand for station number which is the unit id of each device. Whereas the COM # should match the virtual COM port used to establish communication:

The device no. status registers will go HIGH when connected or LOW when a unit is disconnected.