MODBUS RTU type 4x_bit unavailable?
  • HMI Model: cMT-FHDX-220 (HMI cMT-3407)
  • EasyBuilder Pro Version: 6.09.01.605 Build 2024.07.17
  • Serial Number or supplier: 2204105895
  • EasyBuilder Pro User Manual: V6.09.01
MODBUS RTU, Single-Bit Access
EBP User Manual, Section 19.5 MODBUS Address Type, page 804
MODBUS RTU function code 4x_bit
“The function code is the same as 4x. The difference is that 4x_bit reads a single bit in the data.”
Problem: 4x_bit does not appear in the EBP/Numerics Properties/“Address type” drop-down list, so do not find a way to specify/use 4x_bit. (type 4x_32bit does appear, but MODBUS RTU is 16-bit.)
Screenshots included.
Thx!
Address Types
Hi @JimWalls,
Thank you for contributing to our forum! Please note that objects only support address types that are compatible with their format. For example, a word-type address can only be referenced by a word-type object, such as a Numeric or ASCII object.
Similarly, bit-type addresses like 4X_bit can only be referenced by bit-type objects, such as a Toggle Switch or Set Bit. A bit-type address cannot be referenced by a word-type object like a Numeric object.
Note: This methodology applies to tag-based PLCs as well