- HMI Model: cMt3162X
- EasyBuilder Pro Version:V6.08.01.579
- Serial Number or supplier: 2209106203
Trying to figure out if there is a way to create a popup screen when a alarm is triggered.
Popup alarm screen?
none
0.0
0
It can be achieved by using the “Acknowledge Value” within the Event Log and combining it with an Indirect Window object.
Please watch the following two clips from this video called " EasyBuilder Pro Event (Alarm) Log - Weintek USA, Chapter 7".
12:35 – Acknowledge Value (Pop-up Messages)
23:09 – Pop Up window (Acknowledge Value)