- HMI Model: cmt-g02
- EasyBuilder Pro Version:6.10.01
- Serial Number or supplier:
Does anyone have sample a import tag file for mitsubishi FX3G ?
regards
regards
As depicted within our connection guide, you can export your tags from GXWork 2 and save it as a CSV file.
hello i have a no tag found error message when i try to import the csv file
Could you take screenshots of the following?
By the way, the FX3G PLC is a register-based controller. Using a tag file exported from the PLC IDE is not necessary. Instead, you can select the memory type that you need when creating objects in your EBpro project.
Thanks i will use the direct memory mapping solution
Do you think that it is possible to access with a cmt-g02 to the Fx3G CPU but throuht the Beijer HMI E1063 ?
It seems to me that the Beijer HMI E1063 is one of the Beijer’s legacy HMIs. It may have a dedicated driver for the FX3G communication protocol. You can reach out to Beijer technical support team for detailed instructions. I guess E1063 doesn’t have OPC UA Client to consume OPC UA tags from the CMT-G02.
To my knowledge without a Modbus gateway configured inside the Beijer’s HMI, it is impossible to achieve what you’re planning to do. You may reach out to Beijer to see if this HMI allows you to configure a Modbus gateway driver in which you will have to map the FX3G registers to the Modbus RTU registers. This way the G02 will pull Modbus RTU data out of the HMI, and the HMI will act as a gateway in this application.
thanks timWusa this is my B plan, i already test it with a modbus tcp connection on the HMI, i was just wondering if i could do it without modifying the screen program