Hey there, I am setting up the Weintek codesys controller with an EtherCAT Yaskawa servo drive.
I can get to the point where I can enable the drive, but I can’t achieve any motion. My assumption is that I have a simple parameter like maximum torque set to 0 or something of that nature.
The difficulty I am having is finding where those parameters are in the IDE with the weintek codesys library. Ordinarily all the axis parameters can be found in one spot but this seems less intuitive.
I have watched the weintek motion webinar several times, but the demonstrator doesn’t seem to go over where these parameters would be.
I have poked around the example programs as well but they didn’t provide any clarity.
Info is as follows:

Codesys 3.15.10
EtherCAT master 3.15.12

I have the same problem, any solution?

Hi @laspsieca

To configure EtherCAT parameters, please visit the “Startup Parameters” tab of the EtherCAT device as in the example below:

  1. Click the “Add” button to add additional parameters:

  1. To add a parameter, expand an index and select the desired parameter from the sub-index list:

  1. Configure the “Value” and click “Ok” to add this parameter:
    Note: In this example 0: Close, 1: ±10V, 2: ±5V, 3: 1-5V, 4: ±20mA, and 5: 4-20mA. Thus, channel 0 is configured to output 2: ±5V.*

Our Codesys runtime doesn’t support SoftMotion, and the Codesys runtime may not support all 3rd party EtherCAT servo drives out of box. You can reach out to your local distributor to know if our Codesys runtime fits your motion control application. If your local distributor has no idea, they should be able to consult with Weintek.