Hi,
I have this macro in which i have 3 time delays , the first work fine but the 3rd time delay doesn’t seem to be working.
any ideas?
Hi,
I have this macro in which i have 3 time delays , the first work fine but the 3rd time delay doesn’t seem to be working.
any ideas?
Hi @gary14,
Can you please post a picture of the variable declarations within your macro as well and advise as to what version of EasyBuilder Pro you are using?
Hi @gary14,
The max value of a signed short integer or “short” is 32676. The values 240000 and 300000 are out of range, please use an “int” to hold numbers of this size.
That did it ! thanks
Is there a limit of macros that can be running at the same time ?
We do not limit the number of macros that can run at the same time and as of 6.05.01.379 a cMT(X) series HMI supports up to 500 macros.